Need inputs regarding borewell yield , pump selection for 22 apartment complex in Bangalore, Karnataka

Dear Experts,

I am absolutely confused with inputs I get from  A) Driller B) Plumbing consultant C) Pump vendors .

Please get me out of this utter confusion,  I would  rally appreciate if you could provide your insights as to, what is the best approach.

Requirement :  We need  water for 22 Apartments   we  have claculated  as  bare Minimum  22,000 LPD( 5 per unit  x 22 x 100L per head)

 2 Bore wells :  1st in SW and 2nd in NE

*Bore well 1-(Recommended by hdrologist) :

Drilled depth - 800 feet , water touch on - 150 & 335 feet ,Yield  as per driller - 1.25 to 1.5 inch

Plumbing consultant inputs >>- 5.25lpm, Installion depth - 720 feet,  Pump - 7.5 HP, 15 stages, 30lpm at 720 feet, 1.25 HDPE pipe

 pump Vendors ->> 2500 lph ( as per performance chart) - 750 feet,  Pump - 5 HP, 37 stages, 1.25 inch( outer dia) HDPE with rope or 1.25 inch(Column pipes)

->>3500 lph ( as per performance chart) - 750 feet,  Pump - 5 HP, 50 stages,  1.5 inch( outer dia) HDPE with rope or 1.25 inch(Column pipes)

->> 4500 lph ( as per performance chart) - 750 feet,  Pump - 7.5 HP, 45 stages,   1.5 inch without rope (column pipes)

 driller recommendation ->> 3HP, 37 stage, 1.5 inch pipe

Bore well 2-(Recommended by coconut wala) :

Drilled depth - 900 feet , water touch on - 500 & 580 feet ,Yield  as per driller - 0.5 to 0.75

~ driller recommensation ->>  use compressor pump with , 0.5 to 0.75 inch pipe

Note : I understand that the HDPE is based on outer dia  i.e  if I need to get an internal dia of 1.25, I should use 1.5 inch pip, whereas on column pipes the internal dia is exact and hence for 1.25 inch i should procure 1.25 inch.

I am given to beleive that  for  HDPE you need rope and for column you don't need rope .

Thanks in advance  for any inputs....